bark
Member
- Location
- Washington
I have a 400 amp single phase service that is quite old, 20-25 years. Its been flooded a couple of times, and I don't know who has done any work on it previously. I was called to replace a service lateral that was somehow damaged. The cold water bond was terminated in the CT cabinet, not in the two 200 amp disconnects. They are fused with a neutral bar, two lug. The correction that was written says that the cold water bond shall not be terminated on a enclosure, but on the grounded termination point. Are there neutral bars made for Sq D 200 amp disconnects that will accept two 2/0 and 2 #2 wire plus the ground rod wire?
I think it is correct that we can't term the cold water bond in the CT can.
I think it is correct that we can't term the cold water bond in the CT can.