400 amps underground service 280' from transformer to meter

Merry Christmas

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
IF your calculated load is actually 350 amps (rare on residential), to maintain a 3% voltage drop you would need parallel 300 kcmil AL and, if you don't reduce the neutral, it would take a 3" PVCconduit (assuming there is some Sch 80)
And a 280 ft pull with parallel 300’s would need a tugger, good helpers and spool set up
Does anyone know if the POCO was providing this run, what size they would use?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
And a 280 ft pull with parallel 300’s would need a tugger, good helpers and spool set up
Does anyone know if the POCO was providing this run, what size they would use?
agree,,, at a true 350 amp load there is a lot involved.
I was not recommending, simply answering the OP's question based on his input.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
the other way around for me. The idea of the Poco pulling conductors to the meter socket baffles me, I think I've seen it once in
25 years!
Then this will really blow you away. We dig all the way to the Meterbase, install the conduit, and the conductors. 😅
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Then this will really blow you away. We dig all the way to the Meterbase, install the conduit, and the conductors. 😅
When I was working in your area that was normally the case. (y)
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
If it is "from the transformer "then according to 450.3 Overcurrent Protection (B) the secondary breaker rating has to be 125% of transformer rating, in my opinion.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
When I did a job in Tennessee, You put in the conduit, pull string, and the utility would pull the wire ( Volunteer Electric) BREMC, you stub down a pipe and 90, and they dig in and connect to the meter.
 

nizak

Senior Member
customer needs at the end around 350 amps
Is this a value you’ve determined with a load calculation or an uninformed homeowner telling you that?

Curious as to the size of the dwelling and what specific equipment ( EV / On demand water/ Back up electric heat strips for GEO, etc.) are being installed.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
When I did a job in Tennessee, You put in the conduit, pull string, and the utility would pull the wire ( Volunteer Electric) BREMC, you stub down a pipe and 90, and they dig in and connect to the meter.
That's one of the POCOs I deal with. It's actually VEC." Volunteer Energy Cooperative".
 