And a 280 ft pull with parallel 300’s would need a tugger, good helpers and spool set upIF your calculated load is actually 350 amps (rare on residential), to maintain a 3% voltage drop you would need parallel 300 kcmil AL and, if you don't reduce the neutral, it would take a 3" PVCconduit (assuming there is some Sch 80)
Does anyone know if the POCO was providing this run, what size they would use?