I don't think cord reels have a frequency rating.
So far, frequency is not relevant to your question.
But, why would a cord-reel cord be in a raceway?
Skin effect isn't going to be significant. The skin depth at 400Hz will be almost triple the radius of a 10-gauge copper wire.
And nothing in the code singles out different frequencies. The voltage & current dictate the materials & techniques; frequency is irrelevant.
I meant 115Vac, 30A, 400hz coming out of the panel
It will be alumunium wire.
Is Article 400 has cable suitable for this situation?
Why would you use aluminum wire for 30A?? Where would you even get it?
I read somewhere in different thread that, 400Hz should be in Aluminum
I read somewhere in different thread that, 400Hz should be in Aluminum
"Somebody" might have been "thinking" that the higher frequency would result in higher inductive losses if it were in steel conduit.... somebody may have had the thought that 400Hz should be pulled through aluminum conduit. ...
IN aluminum and using aluminum wire mean two completely different things. Was that other thread here? I think somebody may have had the thought that 400Hz should be pulled through aluminum conduit. I don't agree with that. As far as I'm concerned it doesn't make any difference what you use.
-Hal
"Somebody" might have been "thinking" that the higher frequency would result in higher inductive losses if it were in steel conduit.
But if there's no net current in the bundle of wires in the conduit -- the hot wires are paired with their corresponding return wires -- then there's no net magnetic field generated by the wire bundle and negligible induction losses.
I believe there was planning to use 8ccc in a conduit.