400 overhead riser

Status
Not open for further replies.
lot of varibles.....
residential, commercial, 120/240 volt or other ?, temperature...
 
Commercial 120/240

sorry, in detail that might even lead to additional questions.,.,., but assuming 240/120 single phase with no ambient problems.
We now need to consider load. As David referenced, if the calculated load is 380 amps or less, then 310.16 & 240.2(B) would allow a 500 kcmil Cu
for the phase conductors with a neutral sized per 220.61 but not smaller than 1/0 per 250.24(C)
 