zog
Senior Member
- Location
- Charlotte, NC
I think it's a good point, but that specific breaker doesn't have rating plugs, the adjustments are just built in to the trip unit that is part of the breaker. These are brand-labeled Cutler Hammer Series G breakers. He didn't say if it was TM or ELT, but most likely its TM with a fixed thermal and adjustable mag trip, 140U-K6D. So the thermal trip element, which is what this would be tripping on in 2 hours, is sealed inside the trip unit.
I thought this was an AB 140U K-frame