I was thinking just reading your OP that if the equipment you listed there was all electric equipment - there is a possibility that your 400 amp supply might be a little undersized - depending on details that were not provided. But even if not undersized, you may find you need to transfer both 200 amp panels (if that is the route you choose to go) or you may miss some loads you want to be able to run on standby power. You have enough bigger load items that may not be "critical loads" but seem to have enough of them that they may be too much for a single 200 amp feeder to handle and they would need to be split between both 200 amp branches.I agree, YOUR advice to me ought to end because you are just plain rude. There is always that one guy that has nothing better to do than pick apart somebody else's post looking for a way to criticize......
I have no intention of running a tankless water heater with a generator, didn't YOU catch the part where I said "power only the HWH for 45 minutes to fill the TANK". (regular water heater <30 amps) I will not be powering ANY of the big loads on that list with the generator.
In my current home, the only loads I need to run simultaneously are are the fridge/freezers, well pump, ceiling fans. I get by just fine most of the time with my 3000W Yamaha inverter, which will run quietly all night long on 3 gallons of gas. Occasionally, I will need to power a SINGLE 220V 30A load briefly, such as a TANKED water heater OR a boat lift OR a clothes dryer. When I need to do that I disconnect the Yamaha and connect a 7500W Generac for the duration of the need. It is very loud and guzzles gas. Seems like a hassle, but gasoline is very difficult to get after a storm, propane....impossible. I've had to go two weeks without refueling, so a "smallish" is not a cost cutting measure, it is a necessity. My neighbor was bragging about his 25kW whole house generator setup...till he ran out of propane a couple days into the first storm.
Sounds like an interlock kit on one 200A panel may be the best solution. I don't like the generator subpanel I have now because sometimes the one receptacle I really need that one time isn't on that panel, and you can't add everything to it.
Again this based on not knowing how many watts of instantaneous water heating there is, 7 tons of heat pumps helps some with general load, but we don't know how easy it will be to start those units with a smaller generator without more information or if there is electric back up heat present, how many cooking appliances there are and what size are they (you mentioned both ranges and wall ovens), how large are well pumps (you said there were 2), size of pool pump and possible heater (assume heat pump type heater would be most efficient, not sure if that is what is desired though or what capacity would be for any heater for that matter), hot tub load can vary depending on unit. I have had homes with less items then you mentioned that have more then 400 amps of service supplied to them, electric heating was main item that pushed them over 400 amps though, and had they gone with instantaneous electric water heating - maybe would have bumped them to more then they do have for capacity. Around here you need to heat fresh groundwater at least 65 - 70 degrees to get 125 degree water, maybe not quite as much capacity is needed where you are, but those heaters are still a big load when they are running.