That is incorrect unless there is a local amendment to the NEC. The next size up rule can be applied to branch circuits, feeders, and service conductors. Around here a typical 200 amp service is usually #4/0 Al SE cable.They are under the understanding that your reference for next size up with be for brand circuits, not a service entrance conductor.