Re: 400a service
It seems allowed and usual installations are not always code compliant if you get right down to it.On underground installations it is very common to have parallel feeders to a meter base,but,on overhead (pole mounted services),I would have to say a 400a 320a rated metercan with 600mcm up the mast,,,that is not even usually stocked is not common, or parallel 3/0's up a single mast where the derating factor comes into play and not enough holes in the weatherhead,,,,,or (2) 2" risers with 3/0's to to feed a 400a 320a rated metercan.Although the power company in our area allows 500mcm up the mast for this installation I do not believe this to be correct.By rights I feel like, IWIRE, is correct.Since there is no 400 amp main,although unlikely,there is the possibility that a 400amp noncontinous load could be imposed on this service,500mcm which is rated for 380 amps even though only 20 amps lower is not rated for this,parrallel 3/0's up the mast would be even if derated,,,,,,,Thank you all for your inputs.