Taking over a job and the service doesn't seem legal to me. What they have is a 400(320) meter base with a 400a non-fused disconnect fed with parallel 3/0s from meter to line side. From the load side of the disconnect, they did 2/0 cu to a 200a panel directly on the other side of the wall and another 200a panel about 100' across the building (same building) also fed with 2/0.
If both panels were located in the same room, to my interpretation, it would be legal. The second panel being 100' away, does the tap rule come into play and need to have an OCPD?
I also have an issue with the disconnect as they are disconnecting both grounded and ungrounded conductors with no means of bonding the neutral and EGC. Since it's the first means of disconnect, it must be bonded there right?