It would be interesting to see the diagram on the cover.
Looking up that catalog in the Square-D Digest it appears the entire creature has been severely altered including the removal of a main breaker.
There does not appear to be anything wrong with the panel itself.
The Square D Digest says this 400A panel is rated for (1) factory installed 200A breaker, (1) field installed 200A max breaker, and (4) 2-pole 125A max breakers (200A total load).
The picture, in the Digest, is not specific to this catalog number.
The only visible problem, is the use of 1-pole breakers that Masterinbama pointed out.
You are the "Digest" expert so I won't challenge that.
The way that top buss was in the OP's post made me suspicious, so I entered the catalog number in the on-line Digest and got this:
http://www.downloads.schneider-elec...636&p_Conf=i#http://www.schneider-electric.us
It showed a single main, but, as you say it may not be specific to that particular panel.
View attachment 8817One of my buddies found this new electric service. It is a Sq D CU12L400CN. The single pole breakers at the top buss go to enclosed garage recepts and lights. The 2p 80 feeds a pool sub-panel. The 2p 30 feeds an A/C disconnect(non-fused). The contractor cannot understand why is installation is wrong. Can anyone else explain it to him?:blink:
The 200 amp breaker on the right is the factory installed one. They bend the 3/0 with the hard 90's at the factory. When you install the other 200 in the field your wire is straight from the lugs to the line side.There does not appear to be anything wrong with the panel itself.
The Square D Digest says this 400A panel is rated for (1) factory installed 200A breaker, (1) field installed 200A max breaker, and (4) 2-pole 125A max breakers (200A total load).
The picture, in the Digest, is not specific to this catalog number.
The only visible problem, is the use of 1-pole breakers that Masterinbama pointed out.
It has to do with UL Listings and service entrance requirements.I'm sorry, but what is the problem with the sp's being in there? Is it solely because you're in violation of the 6 disc rule or is it something else?
It has to do with UL Listings and service entrance requirements.
Schneider Electric FAQ website:
Can a single pole breaker be used on a Combination Service Entrance Device?
A single pole breaker can be used as a branch device in the loadcenter section (if applicable) of a CSED device. Only two pole breakers are UL listed to be used as main disconnects.
Yes.Thanks Jim, are the single poles considered "Main disconnects" because there is no main ahead of them, ....
I'm sorry, but what is the problem with the sp's being in there? Is it solely because you're in violation of the 6 disc rule or is it something else?
It has to do with UL Listings and service entrance requirements.
Schneider Electric FAQ website:
Can a single pole breaker be used on a Combination Service Entrance Device?
A single pole breaker can be used as a branch device in the loadcenter section (if applicable) of a CSED device. Only two pole breakers are UL listed to be used as main disconnects.