Hello,
Type a weird scenario i saw on an existing building. You have a 400Amp rated meter that goes to a bus and the bus feeds a 350A Fused disconnect and a 150A fused disconnect (on an exterior of a building that is feeding two difference suites). The cable to the bus is rated for 400Amps.
I believe it looks code compliant as long as the total load is calculated 400Amps or lower. But wouldn't it be better to size the cable for 500A+ and upgrade the meter to 600A incase the tenants increase their load over time? Technically each unit could pull its rated load in this case (349A+149A) without the breaker tripping. Which will exceed the 400Amp cable rating and the meter rating.
Type a weird scenario i saw on an existing building. You have a 400Amp rated meter that goes to a bus and the bus feeds a 350A Fused disconnect and a 150A fused disconnect (on an exterior of a building that is feeding two difference suites). The cable to the bus is rated for 400Amps.
I believe it looks code compliant as long as the total load is calculated 400Amps or lower. But wouldn't it be better to size the cable for 500A+ and upgrade the meter to 600A incase the tenants increase their load over time? Technically each unit could pull its rated load in this case (349A+149A) without the breaker tripping. Which will exceed the 400Amp cable rating and the meter rating.