I don't think that there is any real question as to the intent of the code change. It was made so that UL would change their standard for occupancy sensors and other electronic switching devices to prohibit these devices from using the EGC as a grounded conductor. The intent of the code would require the grounded conductor for the switching circuit to be in the switch box, but the code wording does not support that intent.The confusion is over the fact the lighting circuit does not have a grounded conductor but the control circuit does. Not sure we entirely know the intent in this instance, ...
The way I see it the intent of the of the rule is to require a grounded conductor at each switch or make it possible to add one without making a big mess on the carpet or finished walls; if all the wiring is exposed then that is doable........The intent of the code would require the grounded conductor for the switching circuit to be in the switch box, but the code wording does not support that intent.
Yes, if you can easily add a grounded conductor after the original installation then you don't have to provide one at the time of the original installation. My point is that the rule requires you to provide a grounded conductor for the lighting circuit, and not for the lighting control circuit if one is used. If there is a lighting control circuit, there is no use for the grounded conductor of the lighting circuit to be at the swich location.The way I see it the intent of the of the rule is to require a grounded conductor at each switch or make it possible to add one without making a big mess on the carpet or finished walls; if all the wiring is exposed then that is doable.
I understand that, they did include mentioning if the circuit contains a grounded conductor, they did not mention circumstances where the lighing is controlled via a separate control circuit.I don't think that there is any real question as to the intent of the code change. It was made so that UL would change their standard for occupancy sensors and other electronic switching devices to prohibit these devices from using the EGC as a grounded conductor. The intent of the code would require the grounded conductor for the switching circuit to be in the switch box, but the code wording does not support that intent.
It is a safety issue for someone working on the EGC. Workers do not treat the EGC as an energized conductor and that is what it becomes when it is used as the grounded conductor for the electronics.... If UL decides it is safe to carry necessary current on EGC then it is a UL issue not NEC issue.
No rule that actually says you can use EGC as a grounded conductor may be true, yet there is requirements that a separate grounded conductor must be run when needed. UL maybe was just plain wrong in first place to allow EGC to carry this small current, that seems somewhat harmless, but like has been said, put enough of them on same circuit and now you have a significant amount of current on that EGC.It is a safety issue for someone working on the EGC. Workers do not treat the EGC as an energized conductor and that is what it becomes when it is used as the grounded conductor for the electronics.
UL does not get to change the code, but the issue here is that they were not changing the code when they permitted the EGC to be used as a grounded conductor. I had thought, before this issue came up, that the code had a rule that said you could not use the EGC as a grounded conductor, but there really isn't a rule that actually says that.
but my point is that there is no specific rule that says you can't.No rule that actually says you can use EGC as a grounded conductor may be true, ...
This will be addressed in new Exception #3 for the 2014 code. The grounded conductor will only be required at one switch location where there are multiple switches that control the same light(s). It often takes two or 3 cycles to get a code change correct and to get it correlated with other code sections.404.2 Switch Connections. (A)
Three-Way and Four-Way Switches.
Three-way and four-way switches shall be wired so that all switching is done
only in the ungrounded circuit conductor. Where in metal raceways or
metal-armored cables, wiring between switches and outlets shall be in accordance
with 300.20(A).
Exception: Switch loops shall not require a
grounded conductor.
Exception No. 3: Where multiple switch locations control the same lighting load in an interior room or space, a grounded circuit conductor of the lighting circuit shall not be required at each such location if one has been provided at one or more switching points that is (are) visible from most areas within the room including all principal entry points. Where a switch controls a receptacle load or a lighting load that does not serve a habitable room or bathroom, or where automatic control of lighting has been provided or the switch is not within the lit area, a grounded circuit conductor shall not be required. [ROP 9?89]
I didn't look around for any specific rule myself, and I do believe you and am not suprised, even though it goes against what we were all taught - to almost always separate current carrying grounded from equipment grounding conductors.but my point is that there is no specific rule that says you can't.