Two 3 -way switches one at the bottom of a stairway and one at the top both locations will require a neutral in the switch box correct? Because you can't see the upper level from the switch at the bottom of the stairs. The lower switch at present has no neutral and the upper switch does and the power to the switches is from the upper level so the bottom switch is a switch loop without a neutral.
If I can't replace the 3 wire cable to the lower switch with a 14-2-2 then my alternative would be to feed power into the lower switch from the basement and disconnect the existing feed from the second floor which would give me a neutral in both switch boxes
If I can't replace the 3 wire cable to the lower switch with a 14-2-2 then my alternative would be to feed power into the lower switch from the basement and disconnect the existing feed from the second floor which would give me a neutral in both switch boxes