mwm1752
- Aspen, Colo
Let's throw into arguement another code section that does not stipulate Listed accessory --
210.4 Multiwire Branch Circuits
(B) Disconnecting Means. Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates.
By the comments within this discusion I shoud be able to use a piece of copper, small bolt/nut combo as it does connect single pole breakers together. Now the commentary in the NEC ( don't waste time telling me it is not code) which is inserted by those who write code.
For a single-phase installation, the disconnecting means could be two single-pole circuit breakers with an identified handle tie or a 2-pole circuit breaker, as shown in Exhibit 210.1 (top), or by a 2-pole switch, as shown in Exhibit 210.1 (bottom). For a 3-phase installation, a 3-pole circuit breaker, three single-pole circuit breakers with an identified handle tie,