I recently installed two square D 125 amp main lug sub-panels in a detached building at a residence.
I back-fed the first panel with a 60 amp two pole breaker. This serves as the disconnecting means for the detached structure. I came out of the first sub-panel on the main lugs and landed this feeder on the main lugs of the second sub-panel. Both panels are full because of customer additions.
I just read 408.36 F and it tells me the back-fed 60 amp breaker requires an additional fastener to hold it in place. I haven't stumbled accross this requirement before and have never used an addtional fastener. Have I been wiring my sub-panels incorrectly?