Still comes down to where is the line drawn between feeder and branch circuit when it comes to the grounded conductor.The requirement for feeder neutrals is to carry the unbalanced current or to meet table 250.122, whichever is larger. As long as you do that, I think the question is what code section has been violated. If you don't meet those size requirements, then you've violated 200.4(A).
When I was first in this trade the guy I worked for used to run say 3 #12 ungrounded (on 120/240 single phase) and a #10 neutral. This back when there were almost no handle tie rules. I can remember a few times even putting a neutral bar (on insulating mounts) in a junction box and running say a #6 or even #4 neutral and several ungrounded conductors that all utilized that neutral. A new inspector stopped us from continuing this practice - and we realized it never really was code compliant after pointing out the code(s) that applied. Again this before there was much for handle tie rules which today is just one more section of code to cite. None of those installs ever burned down that I am aware of. Some I know are still there. Main thing is that it is not a proper MWBC, though it may function just fine.