joebell
Senior Member
- Location
- New Hampshire
I am doing a project where the flourescent fixtures are equiped with the orange disconnecting means. The apprentice told me on the lat job they cut these off and just spliced to the ballast wires. I told him I did not think that was correct until I read the Article and came across Exception 5.
I am reading it to say if you have a room that has more than one lighting circuit that the individual disconnecting means is not required as long as you are not leaving the space in total darkness. Is this correct?
I am reading it to say if you have a room that has more than one lighting circuit that the individual disconnecting means is not required as long as you are not leaving the space in total darkness. Is this correct?