Re: 410.16 - Means of Support
Recent experience, as opposed to opinion: We just finished a warehouse conversion, making rooms, where we coincidently installed the ceiling also.
We added no extra wires to either the troffers or grid, and the troffers are secured using only the bend-out tabs. I double-check each one.
You can not raise a troffer without damaging the grid. There was absolutely no issue with either the building or electrical inspections.
Just for info's sake, the main runners are supported every 4 feet and the ends (with the tabs), not sides, of the troffers are on the main runners.