chris kennedy
Senior Member
- Location
- Miami Fla.
- Occupation
- 60 yr old tool twisting electrician
A metal luminaire is hung 12' above the floor in a restaurant. Picture a mag wheel with 3 spokes and 3 plastic A-base lamp holders mounted through the spokes.
Does this luminaire need an EGC attached?
Does this luminaire need an EGC attached?
250.110 Equipment Fastened in Place or Connected by Permanent Wiring Methods (Fixed).
Exposed non?current-carrying metal parts of fixed equipment likely to become energized shall be connected to the equipment grounding conductor under any of the following conditions:
(1) Where within 2.5 m (8 ft) vertically or 1.5 m (5 ft) horizontally of ground or grounded metal objects and subject to contact by persons
410.42 Exposed Luminaire.
(A) Exposed Conductive Parts. Exposed metal parts shall be connected to an equipment grounding conductor or insulated from the equipment grounding conductor and other conducting surfaces or be inaccessible to unqualified personnel. Lamp tie wires, mounting screws, clips, and decorative bands on glass spaced at least 38 mm (1? in.) from lamp terminals shall not be required to be grounded.