I don't recall ever seeing an expected 415 voltage reading on my tester in my 30+ years ... 480 sure ..
It's a big Industry, one can't know and do it all I suppose ..
how is that 240/415 range derived, similar to 120/208 I suppose.
240/415 is just like 277/480, except with only 87% the voltage. It's a wye system, and just like 277/480V, the ratio between the two voltages is sqrt(3). The US and most of North America has the two different standard 3-phase voltages (120/208V and 277/480V), based on the scale of the service. Most of the remainder of the world has a middle ground between these two, deployed for most 3-phase services in any scale.
The 415V really "should be" 416V from how 240*sqrt(3) rounds, so you see these numbers used interchangeably.