Got a site with a bunch of IT equipment (servers, routers, etc). Site is currently 208 wye. Considering an upgrade.
Most of the IT gear is currently 2-pole 208V 60A circuits uconnecting to large power strips. 415/240 would allow for 1 pole per circuit, saving a bunch of panel space not to mention bringing an addition 2kw per circuit, which would facilitate connecting an additional server per circuit.
Eaton makes a nice large 415V UPS, so that isn't a problem. I assume we should approach the PoCo and ask for a 480/277 service and then frontend the UPS with a transformer to get it down to 415/240, but wondering if anyone has actually done a 415 service and if that would make more sense?