4160 Isolation Transformer

Status
Not open for further replies.

spikes2020

Member
Location
Nashville, TN
Closure on this Topic

I thought i'd post what the end results are.

The drive is up and running perfectly with no issues. New feed of 13.8kv hits the tranformer and a new feed of 4160 from it to the drive and the motor.

I have included some links to show the input and output waveform of the drive.

The first image is for full load, the second image is at 50%

The following lines show;
1. Voltage input
2. Current input
3. Voltage output
4. Current output

https://i.imgur.com/DM1b9rE.jpg

https://i.imgur.com/fL0knr2.jpg

Results, there is almost no harmonic, just a bit of a 5th harmonic under 50% load.

Anyway thanks again for everyone's help and i will defiantly use some of you'll advice!
 