422.12

Status
Not open for further replies.

peter d

Senior Member
Location
New England
1.) NEC Section/Paragraph: Article 422.12

2.) Proposal Recommends: add new text

3.) Proposal: Add new text to the exception: and the service receptacle required by 210.63

4.) Substantiation: This will bring 422.12 and 210.63 into agreement. This will also legalize a common field practice of installing a service receptacle, not used for auxillary equipment, to be connected to the line side of the branch circuit feeding the equipment.
 

bphgravity

Senior Member
Location
Florida
Re: 422.12

I don't feel this is a good proposal. Receptacles are not auxiliary equipment directly associated with the heating equipment.
 