We are installing a new piece of equipment and it has heat trace (electric) on it in a couple of places. There are also band heaters, cartridge heaters, tube heaters, etc.
Does 427.22 require GFPD (30ma) protection for all of these types of heaters??
The exception for industrial facilities would not apply, there is no need of continuous operation to assure safe operation of the equipment or process...
The equipment is not a "pipeline" as such, but these heaters are there to elevate the operating temp of various parts of the process...
Whether or not the applications meet the definition of a "vessel" would be an judgement call...