430.22 states that my conductors shall have an ampacity of not less than 125% of the full load current rating taken from the tables.
Given I’m adjusting the ampacity to 125% can I use the 90C column as per 110.14(C)?
Thanks
Given I’m adjusting the ampacity to 125% can I use the 90C column as per 110.14(C)?