Senior Member
- Location
- Baton Rouge
- Occupation
- Electrical Inspector
A vendor supplied drawing is showing 4 motors tapped off a feeder with #12 AWG conductors to the CBs which then feeds the motors at 460V, three phase and 10hp. The feeder is #2AWG. The 12s are not one third the ampacity of the #2 - it’s more like one fourth. Should the number 12’s be upsized to 10’s or am I missing something?
Sent from my iPhone using Tapatalk