430.28 motor feeder taps

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
A vendor supplied drawing is showing 4 motors tapped off a feeder with #12 AWG conductors to the CBs which then feeds the motors at 460V, three phase and 10hp. The feeder is #2AWG. The 12s are not one third the ampacity of the #2 - it’s more like one fourth. Should the number 12’s be upsized to 10’s or am I missing something?


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
don, would the #12s not be permissible under the 10ft tap rule depending on the size of the OCP device :?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
don, would the #12s not be permissible under the 10ft tap rule depending on the size of the OCP device :?
If you meet the conditions of 430.28(1), 12 AWG would be compliant.

I did not address the 10' rule because I assumed the 25' rule based on the "1/3" mentioned in the OP.
 