This discussion came up among a few Engineers in my company. On projects where our Mechanical Engineers provide hydronic VAVS with small fan motors (1/8 HP), we typically circuit multiple 120V VAVs on a single 120V,20A branch circuit. Providing a Cooper Bussman Type "STY" fused @15 or similar. This conforms with 430.53(A) Not Over 1 Horsepower and (1), (2), and (3) listed in that section.
Our Mechanicals provided 208V-2P VAVs that are 1/8 HP on another project and when I brought it up, other EEs has said to use the same approach on a 20A circuit and 15A fused STY type switch. There are a few issues with this since the STY is rated at 125V and Part (A) applies to 120V circuits. Since Part (A) no longer applies, are 208V-2P, 1/8HP VAVs able to be circuited together on a 208V,15A circuit with a non-fused motor rated switch at each unit under Part (B) If Smallest Rated Motor Protected?
1/8HP is not listed in table 320.248 so I cannot verify that the 15A Inverse Time Circuit Breaker is <800% of the rating per 430.52. Calculating the value, it seems that 15A would exceed 800% of the FLA of the motor which would not follow the first sentence of Part (B) "If the branch-circuit short-circuit and ground-fault protective device is selected not to exceed that allowed by 430.52 for the smallest rated motor". Is a smaller fused switch needed at each motor to comply?
Our Mechanicals provided 208V-2P VAVs that are 1/8 HP on another project and when I brought it up, other EEs has said to use the same approach on a 20A circuit and 15A fused STY type switch. There are a few issues with this since the STY is rated at 125V and Part (A) applies to 120V circuits. Since Part (A) no longer applies, are 208V-2P, 1/8HP VAVs able to be circuited together on a 208V,15A circuit with a non-fused motor rated switch at each unit under Part (B) If Smallest Rated Motor Protected?
1/8HP is not listed in table 320.248 so I cannot verify that the 15A Inverse Time Circuit Breaker is <800% of the rating per 430.52. Calculating the value, it seems that 15A would exceed 800% of the FLA of the motor which would not follow the first sentence of Part (B) "If the branch-circuit short-circuit and ground-fault protective device is selected not to exceed that allowed by 430.52 for the smallest rated motor". Is a smaller fused switch needed at each motor to comply?