Hello!
When one sizes SC & GFP for a motor per 430.62 are you required to use the maximum percentage of full load current value in Table 430.52 when determining the size of the OCPD
For example 75HP 208V 3 phase motor = 211A per Table 430.250.
Using an Inverse time circuit breaker if Maximum is required 211 x 250% = 527.5A (600A Breaker required)
I am thinking that is not the case but wanted to be certain.
It states ....not greater than the largest rating or setting of the branch circuit short -circuit & ground-fault-protective device for any motor supplied by the feeder.
If maximum value must be used I would think it would state.......... no less than the largest rating or setting of the branch circuit short -circuit & ground-fault-protective device for any motor supplied by the feeder.
In the end you still need the breaker sized to allow starting of the motor.
Thanks in advance for the replies
When one sizes SC & GFP for a motor per 430.62 are you required to use the maximum percentage of full load current value in Table 430.52 when determining the size of the OCPD
For example 75HP 208V 3 phase motor = 211A per Table 430.250.
Using an Inverse time circuit breaker if Maximum is required 211 x 250% = 527.5A (600A Breaker required)
I am thinking that is not the case but wanted to be certain.
It states ....not greater than the largest rating or setting of the branch circuit short -circuit & ground-fault-protective device for any motor supplied by the feeder.
If maximum value must be used I would think it would state.......... no less than the largest rating or setting of the branch circuit short -circuit & ground-fault-protective device for any motor supplied by the feeder.
In the end you still need the breaker sized to allow starting of the motor.
Thanks in advance for the replies