Hello!
When one sizes SC & GFP for a motor per 430.62 are you required to use the maximum percentage of full load current value in Table 430.52 when determining the size of the OCPD
For example 75HP 208V 3 phase motor = 211A per Table 430.250.
Using an Inverse time circuit breaker if Maximum is required 211 x 250% = 527.5A (600A Breaker required)
I am thinking that is not the case but wanted to be certain.
It states ....not greater than the largest rating or setting of the branch circuit short -circuit & ground-fault-protective device for any motor supplied by the feeder.
If maximum value must be used I would think it would state.......... no less than the largest rating or setting of the branch circuit short -circuit & ground-fault-protective device for any motor supplied by the feeder.
In the end you still need the breaker sized to allow starting of the motor.
Thanks in advance for the replies