ryan_618
Senior Member
- Location
- Salt Lake City, Utah
445.13 tells me that, unless an exception is met, I must have conductors are rated at 115% of the nameplate rating of the generator. So, if I have a 60KVA generator, running at single phase 240, I would have an amperage of 250 amps. I then 115% of that 250 and come up with 287.5 amps. That tells me that I would need a conductor not smaller than 350 Kcmil. My question is, what if the generator has an internal 200 amp breaker in it? Do I still have to size the conductor for 287 amps? If so....why?