ryan_618
Senior Member
- Location
- Salt Lake City, Utah
445.13 tells me that, unless an exception is met, I must have conductors are rated at 115% of the nameplate rating of the generator.  So, if I have a 60KVA generator, running at single phase 240, I would have an amperage of 250 amps.  I then 115% of that 250 and come up with 287.5 amps.  That tells me that I would need a conductor not smaller than 350 Kcmil.  My question is, what if the generator has an internal 200 amp breaker in it?  Do I still have to size the conductor for 287 amps?  If so....why?
	
		
			
		
		
	
				
			 
				
 
 
		 
 
		