450.3(A) MV transformer protection
jim dungar
Wisconsin
PE (Retired) - Power Systems
Makes sense.
But I think I still need a fused disconnect - maybe cutouts? - at least something to isolate each primary against inrush current. Without this all 3 2500kVA transformers will energize at the same time. Surely a single CB can’t handle this amount of current without nuisance trips.
Even if you have protection at each transformer, the single feeder breaker will see all of the simultaneous inrush currents.
Isaiah
Baton Rouge
Electrical Inspector
Yes but I can energize each transformer individually with a (fused) disconnect.
jim dungar
Wisconsin
And what will happen when there is a momentary outage at the utility causing the transformers to reenergize all at the same time?