Even if you have protection at each transformer, the single feeder breaker will see all of the simultaneous inrush currents.Makes sense.
But I think I still need a fused disconnect - maybe cutouts? - at least something to isolate each primary against inrush current. Without this all 3 2500kVA transformers will energize at the same time. Surely a single CB can’t handle this amount of current without nuisance trips.