450.3(A) MV transformer protection

Status
Not open for further replies.

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Makes sense.
But I think I still need a fused disconnect - maybe cutouts? - at least something to isolate each primary against inrush current. Without this all 3 2500kVA transformers will energize at the same time. Surely a single CB can’t handle this amount of current without nuisance trips.


Sent from my iPhone using Tapatalk
Even if you have protection at each transformer, the single feeder breaker will see all of the simultaneous inrush currents.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Even if you have protection at each transformer, the single feeder breaker will see all of the simultaneous inrush currents.

Yes but I can energize each transformer individually with a (fused) disconnect.


Sent from my iPhone using Tapatalk
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Yes but I can energize each transformer individually with a (fused) disconnect.


Sent from my iPhone using Tapatalk
And what will happen when there is a momentary outage at the utility causing the transformers to reenergize all at the same time?
 