lielec11
Senior Member
- Location
- Charlotte, NC
- Occupation
- Electrical Engineer (PE)
So I have a situation where we have a 208V-480V step-up transformer rated 750kVA. On the secondary side the EOR designed it with three (3) OCPDs, 300A, 400A, and 800A. Based on table 450.3(B), including the notes, you are only allowed multiple OCPDs if the total rating of them does not exceed the value for a single device.
750kvA @ 480V = 902A x 1.25 = 1127A ~1200A.
300A + 400A + 800 = 1500A >> 1200A
To me this is a code violation but the DOB missed it in their review and "approved" it. Am I misinterpreting the code here?
750kvA @ 480V = 902A x 1.25 = 1127A ~1200A.
300A + 400A + 800 = 1500A >> 1200A
To me this is a code violation but the DOB missed it in their review and "approved" it. Am I misinterpreting the code here?