I quite often come across a circuit that can be a nuisance.

Example system:

Pump controls, unmanned in remote area, electrical disturbances (lighting, etc.) are substantial, outages are common and therefore generator back up power is present, yet not equipped with ?bump-less? automatic transfer switching. Add to the situation VFDS to further pollute the systems power.

Next derive a 120VAC, 1P control power source from ?sketchy? 480VAC, 3P power. I?ll use a 1kVA encapsulated 480/240-120V 1P transformer (CPT) for this example with a 5A, 2P primary breaker and a 10A, 1P secondary breaker.

The nuisance in the system is the 5A, 2P CPT primary breaker. With so many combinations of power transients and interruptions, the little breaker, when asked to re-magnetize the control transformer, often trips. Even with a C or D trip curve, nuisance tripping is problematic.

Now technically a pair of time delay fuses in lieu of this 5A breaker may be a better solution, however the breaker, serving as both a disconnect and resettable protective device is preferred.

Lastly, I?ll say the wiring from the 480V main to the CPT is only a few feet and is #12.

So to table 450.3(B) I go, to see if the code will allow me to increase the ampacitiy of the CPT primary breaker. It does not, or at least I think it doesn?t.

I generally work on the power quality, surge protection etc. in these systems, but for so many years now, this question always comes up: ?how big a breaker can I put in front of my CPT??

Is there anything in the code or other rules that would allow the 5A breaker to be increased to 8 or 10A? Or is 450.3(B) the answer.
 
46 views and no replies? What, am I too verbose?

OK - One of my other personalities wants to put a 2 pole 10A* breaker on the primary of a 1kVA 480/120V single phase transformer that also has secondary protection

*too big?
 
Find a transformer that complies with note 3 to Table 450.3(B). Or use a larger breaker for the disconnect in series with 5 amp time delay fuses.
 
Don & Marc,

Thanks - I spec'd a UL489 D curve 5 amper, seems to have done the trick. Just one of those situations where I didn't want to battle the "fuse apprehension syndrome"

At any rate, guess I should question words such as "pesky" in my vernacular, but of course on the other hand, who doesn't think better with a degree of levity in their brain.

Now if I could just come up with an idea for a new post that succeeds rather than sucking seeds .....
 