I have a 3 phase, 45kva xfmr - 480 - 120/208. I have overcurrent protection on the primary and secondary. Based on 450.3.B, I see the maximum protection on the secondary as 150A. Does this have to be 150A. or can it be less? My intent is to install a 100A. main breaker in the panel the xfmr is feeding since a 150A. will not fit. I realize by doing this I am not using the full output of the xfmr.
Thanks