I assume you mean aluminum. I would parallel 300 kcm. 250 kcm at 75C is only good for 410 amps.hello,
I'm looking for opinions:
I am going to feed a 450 amp 240 volt 1-phase residential service.
Since 310.15 (B) (6) only goes up to 400 amps -
Would you parallel two sets of 250 kcmil or 300.
The wires will be run in one 3'' PVC conduit.
The Meter can is a 450 transocket
no copper,
I believe that one conduit will require an 80% deduction on the conductors.
But I want to know if I should be using 310.16 or if I can somehow use 310.15 (B) (6)