I had an electrician call me up the other day and ask about the effect of inrush current on a 45kVA transformer and nuisance tripping. He was curious if he could up size the circuit breaker 250%.
After some research and reading an article about inrush current in transformers by Eaton, I came to conclusion that he would be safe with an OCPD at 125%, but if he provided OCP on the secondary side, he could go up to 250% on the primary. Because of the building design, we concluded with his solution to use an OCPD of 250% on the primary at the panel, a fused disconnect within the 25ft tap rule, and an OCPD of 125% on the secondary panel.
Any thoughts about this? I know the extra fuse disconnect sounds redundant, but it was to meet tap rule. Anyone experience nuisance tripping from transformer inrush?
After some research and reading an article about inrush current in transformers by Eaton, I came to conclusion that he would be safe with an OCPD at 125%, but if he provided OCP on the secondary side, he could go up to 250% on the primary. Because of the building design, we concluded with his solution to use an OCPD of 250% on the primary at the panel, a fused disconnect within the 25ft tap rule, and an OCPD of 125% on the secondary panel.
Any thoughts about this? I know the extra fuse disconnect sounds redundant, but it was to meet tap rule. Anyone experience nuisance tripping from transformer inrush?