T triplex15 Member Location Virginia Aug 8, 2008 #1 Can I use 3/0 CU to feed from a generator to a 200amp disconnect then 4/0AL SER to a transfer switch then 4/0AL SER to the 200amp Panel in the house? Also could I down size my ground Wire?
Can I use 3/0 CU to feed from a generator to a 200amp disconnect then 4/0AL SER to a transfer switch then 4/0AL SER to the 200amp Panel in the house? Also could I down size my ground Wire?
jrannis Senior Member Location Fort Lauderdale/ Miami Aug 8, 2008 #2 Sound ok to me. #6 would be the smallest size for the equipment ground
R RUWired Senior Member Location Pa. Aug 8, 2008 #3 triplex15 said: Also could I down size my ground Wire? Click to expand... With SER aluminum conductors, # 4awg would be the minimum size ground allowed. Rick
triplex15 said: Also could I down size my ground Wire? Click to expand... With SER aluminum conductors, # 4awg would be the minimum size ground allowed. Rick