GeorgeB

ElectroHydraulics engineer (retired)
Location
Greenville SC
Occupation
Retired
True, but motor will rarely, if ever see SFA

YOUR motor, perhaps. I deal in the industrial hydraulics world ... it is not at all unusual for a machine to be loaded at 10% for 90% of a cycle, 100% for 9%, and 250% for 1%. That 1% is in the 0.1 to 1.0 sec range as oil is compressed, and a little compression of the workpiece after half of the 100% period.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Yep - I’ve always figured the manufacturers knew what they were doing and never worried about the size of the wires.


So, is it safe to assume motor connection leads for a typical Nema TEFC induction motor must carry at least SFA? And lastly, what standards do manufacturers use as a guideline?
I couldn't find anything in MG-1.
 

retirede

Senior Member
Location
Illinois
So, is it safe to assume motor connection leads for a typical Nema TEFC induction motor must carry at least SFA? And lastly, what standards do manufacturers use as a guideline?
I couldn't find anything in MG-1.

My answer to your 2 questions:

1) Yes (I’ve never seen a failure of motor leads).

2) I don’t know.
 

RichB

Senior Member
Location
Tacoma, Wa
Occupation
Electrician/Electrical Inspector
Does anyone out there know: Are motor connection leads (pigtails inside motor termination box), sized per NEC requirements of motor FLA x 1.25%? My understanding is motor leads are controlled by NEMA but shouldn't basic sizing requirements still apply according to motor HP, S.F., Insulation type etc?

Thanks in advance.

Isaiah.

Contact a motor rewind facility--I am sure they would know where and what the standards are
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Contact a motor rewind facility--I am sure they would know where and what the standards are

Maybe some large shops that are highly organized, other places not so much I bet. We rewound motors for a long time and it was all cowboy engineering when it came to sizing of windings and leads. We would go up in wire gauge and insulation class so there was never a problem.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Maybe some large shops that are highly organized, other places not so much I bet. We rewound motors for a long time and it was all cowboy engineering when it came to sizing of windings and leads. We would go up in wire gauge and insulation class so there was never a problem.

Dave. When you say “we would go up in wire gauge and insulation...” you mean above NEC requirements?


Sent from my iPhone using Tapatalk
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
The standard is for the MOTOR, not the wire size, meaning that if you can get your motor to pass the tests with wire that ends up smaller than the NEC would allow, that's fine, because the entire MOTOR is tested as an ASSEMBLY. But at the same time, a motor designer will not want to take too much of a chance because that testing is expensive and having something fail because you scrimped too much on the conductor size is the kind of thing that gets you a pink slip.

Motor wire manufacturers publish guidelines for their brands of wires to help those motor designers, here is one:
http://www.ecswire.com/mmspecs/Specsheets/Belden/leadWireSelectionChart.pdf

As you will see, using your example of #8s observed in a 40HP motor, #8 per the NEC is good for 50A without any adjustment factors, but for the motor lead wires, using the 3 conductor chart (#3), it's good for 76A if using EDPM 150C lead wire. Even this isn't that simple, there's a lot more to it. Bottom line, again, you can't equivocate the wire sizes used per the NEC to what is used INSIDE of the motor.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
The standard is for the MOTOR, not the wire size, meaning that if you can get your motor to pass the tests with wire that ends up smaller than the NEC would allow, that's fine, because the entire MOTOR is tested as an ASSEMBLY. But at the same time, a motor designer will not want to take too much of a chance because that testing is expensive and having something fail because you scrimped too much on the conductor size is the kind of thing that gets you a pink slip.

Motor wire manufacturers publish guidelines for their brands of wires to help those motor designers, here is one:
http://www.ecswire.com/mmspecs/Specsheets/Belden/leadWireSelectionChart.pdf

As you will see, using your example of #8s observed in a 40HP motor, #8 per the NEC is good for 50A without any adjustment factors, but for the motor lead wires, using the 3 conductor chart (#3), it's good for 76A if using EDPM 150C lead wire. Even this isn't that simple, there's a lot more to it. Bottom line, again, you can't equivocate the wire sizes used per the NEC to what is used INSIDE of the motor.

I contacted Baldor-Reliance regarding this particular motor. According to their documentation the motor leads are #4’s which would vastly exceed the required FLA plus SF. However my observation, along with two other senior electrician tells me they’re really much closer to #8’s.


Sent from my iPhone using Tapatalk
 

kwired

Electron manager
Location
NE Nebraska
Why stop at the motor leads? What about the windings in the stator? They are seeing the same current.

So, is it safe to assume motor connection leads for a typical Nema TEFC induction motor must carry at least SFA? And lastly, what standards do manufacturers use as a guideline?
I couldn't find anything in MG-1.
Also consider your common dual voltage 208-240/480 volt motor has leads that only carry half the motor current when connected in the low voltage configuration. So you supplied the motor with a 4 AWG copper but those approximately 10 or 12 AWG leads are only carrying half the current that the supply conductor is carrying. In high volts connected application the supply conductor maybe only needs to be 8 AWG - closer to the size of the motor leads, which are carrying all the motor current in high volts configuration, but they are higher temp, short length, etc. as mentioned by others and designed for the application.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Also consider your common dual voltage 208-240/480 volt motor has leads that only carry half the motor current when connected in the low voltage configuration. So you supplied the motor with a 4 AWG copper but those approximately 10 or 12 AWG leads are only carrying half the current that the supply conductor is carrying. In high volts connected application the supply conductor maybe only needs to be 8 AWG - closer to the size of the motor leads, which are carrying all the motor current in high volts configuration, but they are higher temp, short length, etc. as mentioned by others and designed for the application.

This particular motor does not have a dual winding. There are only 3 leads.


Sent from my iPhone using Tapatalk
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Also consider your common dual voltage 208-240/480 volt motor has leads that only carry half the motor current when connected in the low voltage configuration. So you supplied the motor with a 4 AWG copper but those approximately 10 or 12 AWG leads are only carrying half the current that the supply conductor is carrying. In high volts connected application the supply conductor maybe only needs to be 8 AWG - closer to the size of the motor leads, which are carrying all the motor current in high volts configuration, but they are higher temp, short length, etc. as mentioned by others and designed for the application.

Motors are not rated 240/480V - they are rated 230/460V.
 

retirede

Senior Member
Location
Illinois
Motors are not rated 240/480V - they are rated 230/460V.

That is standard. We used to have obtuse customers who insisted on 480V nameplate. We would have the motor manufacturer re-nameplate a standard motor and up charge accordingly.

Just pointing out that one may encounter some seemingly oddball ratings in the wild.
 

kwired

Electron manager
Location
NE Nebraska
That is standard. We used to have obtuse customers who insisted on 480V nameplate. We would have the motor manufacturer re-nameplate a standard motor and up charge accordingly.

Just pointing out that one may encounter some seemingly oddball ratings in the wild.
Upcharge not only from you but from motor vendor/manufacturer. This makes every motor you purchase a special order.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Upcharge not only from you but from motor vendor/manufacturer. This makes every motor you purchase a special order.

If you go back far enough, you'll find motors listed as '440V'. This has evolved over the years to the present day '460V' and sometimes, '480V'.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
That is standard. We used to have obtuse customers who insisted on 480V nameplate. We would have the motor manufacturer re-nameplate a standard motor and up charge accordingly.

Just pointing out that one may encounter some seemingly oddball ratings in the wild.