I work in an industrial plant where we use many start/stop stations for electrical motors. I have seen some cases where someone wired the station with the control tapped off L1 and L2 of the motor starter (where the coil of the starter is a 460V coil).
1.) I have been told that it is "code" to limit control voltage to 120VAC max. I have been unsuccessful in finding this written in the 2002 NEC. I have also been told that the practice is acceptable, but that the control circuit must be fused.
If there is a fault in one of the buttons, but no short to ground, there would be approx. 260V potential between a metal part of the button and ground (or the panel, if it is metallic, and grounded).
2.) We have a washdown/refrigerated environment and experience water entering our enclosures and condensation problems, also. I have seen some cases where a pushbutton having a metal locknut will have a 120V potential between the locknut and ground (non-metallic enclosure and 120VAC as control). A-B 800T/800H pushbuttons, specifically.
What is code?
What is safe?
My co-workers are getting shocked by the 120V faults where a NM panel is used. If these panels were metallic, I am sure our breakers would be tripping constantly.
3.) Are mineral deposits penetrating these pushbuttons, and making them conductive where they should be insulated? Perhaps rubber boots over the PB's would be a solution.
Before we have a serious shock, with someone being seriously hurt (120 bad enough, let alone 240 or 460).
Thanks in advance for any help.
bp
1.) I have been told that it is "code" to limit control voltage to 120VAC max. I have been unsuccessful in finding this written in the 2002 NEC. I have also been told that the practice is acceptable, but that the control circuit must be fused.
If there is a fault in one of the buttons, but no short to ground, there would be approx. 260V potential between a metal part of the button and ground (or the panel, if it is metallic, and grounded).
2.) We have a washdown/refrigerated environment and experience water entering our enclosures and condensation problems, also. I have seen some cases where a pushbutton having a metal locknut will have a 120V potential between the locknut and ground (non-metallic enclosure and 120VAC as control). A-B 800T/800H pushbuttons, specifically.
What is code?
What is safe?
My co-workers are getting shocked by the 120V faults where a NM panel is used. If these panels were metallic, I am sure our breakers would be tripping constantly.
3.) Are mineral deposits penetrating these pushbuttons, and making them conductive where they should be insulated? Perhaps rubber boots over the PB's would be a solution.
Before we have a serious shock, with someone being seriously hurt (120 bad enough, let alone 240 or 460).
Thanks in advance for any help.