480-240 single phase ground point

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
On a single phase 480-240 v transformer supply utilization equipment that does not carry a neutral.

Would it be proper to ground the X2-X3 junction like a typical 120/240 system.

Would it be proper to ground X4.

Would one be more advantageous than the other in this application

Please see pic
 

Attachments

  • IMG_7492.png
    IMG_7492.png
    1.3 MB · Views: 11

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
I was trying to think of fault current and to my imperfect thinking I thought either could be ok.

If I am correct you recomend X2-3 junction
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I was trying to think of fault current and to my imperfect thinking I thought either could be ok.

If I am correct you recomend X2-3 junction
An end-grounded arrangement would double the line-to-ground voltage, increasing fault current.

I do, for all the usual reasons.
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
An end-grounded arrangement would double the line-to-ground voltage, increasing fault current.

I do, for all the usual reasons.
Thank you very much great explanation. I felt both gave a path, but did not think of the increased fault current on corner ground.
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
The other reason for grounding the center tap (X2-X3) is to limit the line to ground voltage to 120. This is because lots of things that might work on 240 do not like 240 line to ground due to transient protection, etc.
Thank you
 