Hello everyone. I would like to get some clarification on transformer installations for servicing a machine.
We have a machine to be installed requiring 200 to 240 volts 3 ph. 97 kva We have 480v from a fused buss plug that would be run down to the transformer, along with an egc that goes to a common plant grounding grid. then out of the transfomer to a fused disconnect then to the machine ocpd.
Now i believe a delta/wye 480/208 would provide a very simple and safe installations bonding the neutral secondary tap to the transformer frame and equipment grounds.
my question is how would you install this system with a 480/240 delta/delta xformer, to include meeting all code requirements, and grounding/bonding to our plant grounding grid? A delta secondary causes confusion for many, including myself and that is why I am posting because I want to be confident in answering any questions.
I am aware that you can install the machine as ungrounded supplied from the delta secondary. does this infact mean that if the delta is not corner grounded any EGC wiring would be worthless? You would only see phantom voltages from capacitive coupling to ground. some of my questions come from viewing another similar machine that is infact using a delta/delta xformer., and there is no ground fault detection, i am questioning if this is even safe or correct to use.
What if the machine builder requires 240 3 phase, and 208v is considered too low, then a delta would be the only option?
I would appreciate if someone could single line the two different installations and ground connections so it is safe, protected from lightning/voltage problems etc.
thanks,
steve
We have a machine to be installed requiring 200 to 240 volts 3 ph. 97 kva We have 480v from a fused buss plug that would be run down to the transformer, along with an egc that goes to a common plant grounding grid. then out of the transfomer to a fused disconnect then to the machine ocpd.
Now i believe a delta/wye 480/208 would provide a very simple and safe installations bonding the neutral secondary tap to the transformer frame and equipment grounds.
my question is how would you install this system with a 480/240 delta/delta xformer, to include meeting all code requirements, and grounding/bonding to our plant grounding grid? A delta secondary causes confusion for many, including myself and that is why I am posting because I want to be confident in answering any questions.
I am aware that you can install the machine as ungrounded supplied from the delta secondary. does this infact mean that if the delta is not corner grounded any EGC wiring would be worthless? You would only see phantom voltages from capacitive coupling to ground. some of my questions come from viewing another similar machine that is infact using a delta/delta xformer., and there is no ground fault detection, i am questioning if this is even safe or correct to use.
What if the machine builder requires 240 3 phase, and 208v is considered too low, then a delta would be the only option?
I would appreciate if someone could single line the two different installations and ground connections so it is safe, protected from lightning/voltage problems etc.
thanks,
steve