Hvac installer put in a 208/240 3/0 unit. I have 480/277 3/0.
Wed a transformer. Seems since they’re no neutral to this unit that 240volt delta 3/0 would be best.
Just want to double check.
 
Seems since they’re no neutral to this unit that 240volt delta 3/0 would be best.

Although you don't need a neutral, a 480 - 240/139V transformer is another possubility. It gives you balanced L-G voltages in case there is circuitry in the unit that could be sensitive to this, for example MOV surge suppressors in a VFD. If that was true, though, I'd expect the installation instructions to mention it.

 
HVAC systems are becoming more inverter based, and inverters prefer grounded wye supplies.

This is not as much a problem in the 200V class, but something to consider.

I'd probably go with 208/120V unless there was a performance hit or significant wiring cost change.
 
Even though the unit does not need a neutral, it may have a drive. I would go with a 120.240 secondary so you will have the neutral reference.
(or the two previous posts that popped up as I as typing :) )
 
Even though the unit does not need a neutral, it may have a drive. I would go with a 120.240 secondary so you will have the neutral reference.
(or the two previous posts that popped up as I as typing :) )
I am surprised by how many electricians become somewhat confused when they have to work on systems that do not have 'solid' Line-Neutral and Line-Ground connections tions, so I like to include neutrals.
 