Hi Folks -
Scenario
Large apartment complex receiving primary voltage 4160 three phase. Voltage is stepped down by customer owned transformers to 240V delta (for motor loads) and to three 120/240 V single phase (each feeding a distribution board). Largerst billed demand is 180 kW.
The customer wants to investigate backup power with generator and transfer switch.
Customer has received quotes for 240 generator and transfer switches.
Possible alternative solution...
Install 4160 V transfer switch
Feed switch with utility and generated 4160.
4160 volt generator is big buck$$$.....so...
Here are the questions:
If 480 V generator, say 300kW with it's 480 V breaker is fed to the supply side primary of a 480-4160V ~300kVA transformer and then to the 4160 V transfer switch. The primary is the supply side (per Code).
What NEC table would be used to size overcurrent protection? 450.3(A) or 450.3(B)? Neither seems to apply for a stepup transformer for sure....
Would the transformer be delta-delta? and if so, does this allow 240.4(F) be used to protect the secondary conductors?
Any experience or caveats?
Bill
Scenario
Large apartment complex receiving primary voltage 4160 three phase. Voltage is stepped down by customer owned transformers to 240V delta (for motor loads) and to three 120/240 V single phase (each feeding a distribution board). Largerst billed demand is 180 kW.
The customer wants to investigate backup power with generator and transfer switch.
Customer has received quotes for 240 generator and transfer switches.
Possible alternative solution...
Install 4160 V transfer switch
Feed switch with utility and generated 4160.
4160 volt generator is big buck$$$.....so...
Here are the questions:
If 480 V generator, say 300kW with it's 480 V breaker is fed to the supply side primary of a 480-4160V ~300kVA transformer and then to the 4160 V transfer switch. The primary is the supply side (per Code).
What NEC table would be used to size overcurrent protection? 450.3(A) or 450.3(B)? Neither seems to apply for a stepup transformer for sure....
Would the transformer be delta-delta? and if so, does this allow 240.4(F) be used to protect the secondary conductors?
Any experience or caveats?
Bill