480 to 600 Transformer help - for testing a system

Status
Not open for further replies.

emiller233

Senior Member
Location
pittsburgh, pa
We have a system that we will need to test to pass a SPE-1000 certification thru Intertek.

This system will operate in Canada or in the USA, so it is designed to run on both: 600VAC, 3-phase as well as 480. There is a 75KVA transformer (Delta to Wye) on the machine to drop the voltage down to 480VAC when in Canada. So if the system is in the USA, they will not use the transformer and wire it to 480.

My question is for the SPE-100 testing we need to run this thing at 600VAC to pass the inspection.

Can we use our shops 480V and run it thru a 480V to 600V step up 75KVA transformer (just for during the inspection)? Would this need to be another delta-WYE transformer? What about the grounding?

i attached a picture of the current transformer wiring (600V to 480V)
xfmr.jpg
 

ron

Senior Member
You can use your shop's 480V and run it thru a 480V to 600V step up 75KVA transformer. If you could get a Delta Wye (where 480V is the Delta and 600V is the Wye) and bond the X0 of the Wye to the Ground (separately derived service), then feed 3 phase conductors and an equipment grounding conductor to the equipment's step down transformer.
 

emiller233

Senior Member
Location
pittsburgh, pa
You can use your shop's 480V and run it thru a 480V to 600V step up 75KVA transformer. If you could get a Delta Wye (where 480V is the Delta and 600V is the Wye) and bond the X0 of the Wye to the Ground (separately derived service), then feed 3 phase conductors and an equipment grounding conductor to the equipment's step down transformer.


PERFECT! thanks for the help and the quick reply also!
 

mike_kilroy

Senior Member
Location
United States
If it was me, I would NOT waste the extra money on the D-Y xfmr since I already will be using the one in the machine!

I would simply buy a 3ph 480/600 volt auto xfmr.

75kva is d-y about $ 6000.00, but auto about $ 3000.00.

Depending where u r, if in canada, Rex xfmr is good place, if in us midwest, controlled magnetics, mi. Or equiv.

Sent from my SM-G900V using Tapatalk
 

emiller233

Senior Member
Location
pittsburgh, pa
If it was me, I would NOT waste the extra money on the D-Y xfmr since I already will be using the one in the machine!

I would simply buy a 3ph 480/600 volt auto xfmr.

75kva is d-y about $ 6000.00, but auto about $ 3000.00.

Depending where u r, if in canada, Rex xfmr is good place, if in us midwest, controlled magnetics, mi. Or equiv.

Sent from my SM-G900V using Tapatalk

I've never used an auto transformer, or even know much about them. Quick Google search says it's just a single core transformer with multiple taps one both like e &load side. Is that accurate?

Are there any other pros/cons to using one of these?

Do you just ground the chassis of the auto transformer to the shop supply and the system this is powering up?

I've got quotes back for a d-y transformer, and they are pretty long lead times. So I am looking for any alternative that I could possibly get faster. Cheaper and smaller is always good! So I'm liking the sounds of this auto transformer

I'm am in the USA (Pennsylvania), so I don't know if I could use your supplier. I will certainly check into it tho!
 

Electric-Light

Senior Member
What does the machine do and is this something you are integrating or just testing for a client?

If there's a difficult to start motor load or there is a solid state controlled load of industrial nature, you should be using a source with impedance percent that is reasonably similar to where the machine will be installed. When you run something that calls for close to 75kVA behind two layers of 75kVA transformer, dynamics from machine's perspective can be dramatically different from direct connection to a branch fed from a 750kVA utility transformer. The available fault current behind two layers of miniature transformers compared to a utility source will likely be an order of magnitude different from the utility source and functions related to fault protection would be invalid.

You get a 2kW portable generator. Plug a microwave into it. Theoretically, it should be able to handle anything that goes into a 15A outlet. Well in actuality, the second you hit start, there is a good chance that the computer will drop out.

If you just need it for a short while, you might be better off hiring a mobile substation service used by facilities and utilities during lead time or while repairs are being made. Perhaps try calling companies that do carnival or festival setup. Surely they've run into times when the site power doesn't mesh up with their rides.
 
Last edited:

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Note that to use a three phase autotransformer it pretty much has to be a wye configuration.
A "delta autotransformer" is a strange eccentric beast that "ungrounds" a corner grounded delta. Avoid it.

Sent from my XT1585 using Tapatalk
 

mike_kilroy

Senior Member
Location
United States
1) I've never used an auto transformer, or even know much about them. Quick Google search says it's just a single core transformer with multiple taps one both like e &load side. Is that accurate?

2) Are there any other pros/cons to using one of these?

3) Do you just ground the chassis of the auto transformer to the shop supply and the system this is powering up?

4) I've got quotes back for a d-y transformer, and they are pretty long lead times. So I am looking for any alternative that I could possibly get faster. Cheaper and smaller is always good! So I'm liking the sounds of this auto transformer

5) I'm am in the USA (Pennsylvania), so I don't know if I could use your supplier. I will certainly check into it tho!

1) "just a single core thng" is a pretty bad description. Most transformers have a "single core" for each phase so that is no unique description for autoxfmr... multiple taps is good sttatement though. Yes, each phase is wound around single core just like an isolation 9iso) xfmr. And just like a typical iso xfmr primary winding, it has "multiple taps." The auto xfmr just stops there: it does not have a secondary winding. Finished. Done. That's all folks. Just a primary winding. So yes, a single winding [per phase] with taps. In your case at 480v and at 600v. Looks just like an iso xfmr. Reason it is cheaper it is just the pri winding, no cost for a secondary winding, and its physical size is reduce to (1-480/600)*75= 15kva physical size; hence you are paying for basically a 15kva xfmr instead of a 75kva.

2) pros and cons? sure some potential ones already mentioned by other replies. But none of these re likely to effect you at all. Consider: your 75kva xfmr probably has Z (impedance) of about 5%. An auto xfmr has much lower Z than an equi iso, so you may be adding 2% more with it in series. Unless your machine uses some unique requirement servos such as Siemens, that require <3% Z input, this added 2% certainly won't bother it. Especially for just a single test. Sure it is a Y configuration, but like an induction motor, whether it is Y or D config, it has no meaning to you - it is simply going to be used as a voltage change device. Either will do the job as well and as transparently to you and your machine.

3) No ground required or used; sure you can ground the metal "core" - there is likely a ground terminal on it for you.

4) Suggest you ask them what they have in stock that can do your job; often they have something. As xfmr supplier, we often can get something required if needed quick so you should be able to - if you ask.

5) Both places I posted ship worldwide. Many many others do too.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
An 'autotranformer' is one where there is a single coil (note: single for a phase) with multiple taps for your input and output voltages, rather than separate primary and secondary coils.

A single phase transformer with separate primary and secondary coils can be connected as an autotransfomer; this is the common practice with so called buck-boost transformers.

The huge benefit of using an autotransformer configuration is that only part of the power goes through the transformer, so you don't need the full kVA rating.

For 3 phase use, you could use 2 or 3 single phase transformers, connected as autotransformers.

For your application, I think you could use a set of 3 480V to 120V 10 kVA transformers to boost 480V to 600V with a net capacity in excess of 75 kVA (you only need 5kVA 277 to 70V transformers, but 480 to 120 is a standard rating and likely cheaper). You would need to have an engineer or the transformer supplier do a detailed design.

-Jon
 

topgone

Senior Member
. . . . . . . . . . . . . . . . . . .

For your application, I think you could use a set of 3 480V to 120V 10 kVA transformers to boost 480V to 600V with a net capacity in excess of 75 kVA (you only need 5kVA 277 to 70V transformers, but 480 to 120 is a standard rating and likely cheaper). You would need to have an engineer or the transformer supplier do a detailed design.

-Jon

3 X 10kVA transformers to be connected into 480/600V autotransformer? 480V single-phase transformers connected in wye will be underfluxed when supplied with 480V line-to-line voltage!(supply voltage will be 277V).

You could use 480/120V single-phase transformers if you wired it open-delta. You only need two-10kVA, 480/120V transformers! Max amps = 83A @ 600V (86.6 kVA)
 

emiller233

Senior Member
Location
pittsburgh, pa
What does the machine do and is this something you are integrating or just testing for a client?

this machine is fairly basic, it is a 'Test Bench' for testing an Air Compressor off of a train.
this transformer will power up a 480V 3-phase air conditioner (3.4FLA) and a large 330VDC Power supply (30KW) http://www.signaltestinc.com/product-p/sga 330-91.htm. Off the top of my head, this thing takes around 41A (I'd have to double check that #). so i need about 50A total

the control circuits are thru a separate 120VAC feed...

we looked into a mobile generator, and are willing to do this (that was priced into the job). the only thing is we may need to keep it much longer than we thought so the price would be quite a bit higher. that's why we are looking into using a transformer (that we could also use in the future if needed)
 
Last edited:

emiller233

Senior Member
Location
pittsburgh, pa
1) "just a single core thng" is a pretty bad description. Most transformers have a "single core" for each phase so that is no unique description for autoxfmr... multiple taps is good sttatement though. Yes, each phase is wound around single core just like an isolation 9iso) xfmr. And just like a typical iso xfmr primary winding, it has "multiple taps." The auto xfmr just stops there: it does not have a secondary winding. Finished. Done. That's all folks. Just a primary winding. So yes, a single winding [per phase] with taps. In your case at 480v and at 600v. Looks just like an iso xfmr. Reason it is cheaper it is just the pri winding, no cost for a secondary winding, and its physical size is reduce to (1-480/600)*75= 15kva physical size; hence you are paying for basically a 15kva xfmr instead of a 75kva.

2) pros and cons? sure some potential ones already mentioned by other replies. But none of these re likely to effect you at all. Consider: your 75kva xfmr probably has Z (impedance) of about 5%. An auto xfmr has much lower Z than an equi iso, so you may be adding 2% more with it in series. Unless your machine uses some unique requirement servos such as Siemens, that require <3% Z input, this added 2% certainly won't bother it. Especially for just a single test. Sure it is a Y configuration, but like an induction motor, whether it is Y or D config, it has no meaning to you - it is simply going to be used as a voltage change device. Either will do the job as well and as transparently to you and your machine.

3) No ground required or used; sure you can ground the metal "core" - there is likely a ground terminal on it for you.

4) Suggest you ask them what they have in stock that can do your job; often they have something. As xfmr supplier, we often can get something required if needed quick so you should be able to - if you ask.

5) Both places I posted ship worldwide. Many many others do too.


1) this is the one i am currently looking at. Hammond Power # Y075QTC https://www.hammondpowersolutions.com/product/hps-autotransformers/

2) i looked quickly thru the spec sheet that this Transformer will be powering, didn't see anything specifying this http://www.signaltestinc.com/v/vspfiles/assets/datasheet/Sorensen_SG_Datasheet.pdf

4) so far this morning, I've reached out to Eaton (they wont talk about expediting until they have a P.O.) and waiting to hear back from Hammond Power, hopefully they have something available

5) I am going to look into these and get quotes from them as well!
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Your system under test has an input delta-wye transformer. This will pretty much isolate it from whatever the supply grounding is. In other words you input transformer would probably work just fine with a wye supply (600/346V), a 'high leg' , a 'corner grounded' system, or something else.

Your test specifications may limit the allowed supply, for example requiring a wye system balanced around ground potential or some other limiting factor.

The most blog standard approach would be a delta-wye isolating transformer, with the neutral of the wye grounded.

Autotransformer approaches will let you use smaller and off the shelf transformers, but this really needs to be engineered by a transformer supplier, not a web forum.

I suggested one possibility which gives an output balanced around neutral; topgone suggested one that is more efficient.

You won't find a 'delta-wye' autotransformer; since you don't have separate primary and secondary coils you have either delta or wye, not both at the same time.

-Jon
 

emiller233

Senior Member
Location
pittsburgh, pa
An 'autotranformer' is one where there is a single coil (note: single for a phase) with multiple taps for your input and output voltages, rather than separate primary and secondary coils.

A single phase transformer with separate primary and secondary coils can be connected as an autotransfomer; this is the common practice with so called buck-boost transformers.

The huge benefit of using an autotransformer configuration is that only part of the power goes through the transformer, so you don't need the full kVA rating.

For 3 phase use, you could use 2 or 3 single phase transformers, connected as autotransformers.

For your application, I think you could use a set of 3 480V to 120V 10 kVA transformers to boost 480V to 600V with a net capacity in excess of 75 kVA (you only need 5kVA 277 to 70V transformers, but 480 to 120 is a standard rating and likely cheaper). You would need to have an engineer or the transformer supplier do a detailed design.

-Jon

i am going to look into this. i am not familiar with buck-boost transformers either. this sounds like a good solution as well.

wouldn't a 480V to 120V be a different ratio than 600V to 480V?
 

emiller233

Senior Member
Location
pittsburgh, pa
3 X 10kVA transformers to be connected into 480/600V autotransformer? 480V single-phase transformers connected in wye will be underfluxed when supplied with 480V line-to-line voltage!(supply voltage will be 277V).

You could use 480/120V single-phase transformers if you wired it open-delta. You only need two-10kVA, 480/120V transformers! Max amps = 83A @ 600V (86.6 kVA)

i've never wired on in open delta, so i did a quick google search and was reading about it here http://myelectrical.com/notes/entryid/254/what-is-an-open-delta-transformer
i am still confused how to do the calculation to get these numbers
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
i am going to look into this. i am not familiar with buck-boost transformers either. this sounds like a good solution as well.

wouldn't a 480V to 120V be a different ratio than 600V to 480V?

Look at the wiring diagram for the hammond autotransformer you are considering.

Like most 3 phase transformers it can be considered as a set of 3 single phase transformers connected together.

Each of the transformer legs is a 277V to (277+69)V autotransformer leg. You don't have a separate primary and secondary circuit; the secondary voltage gets derived magnetically but then _added_ to the primary voltage. The transformer is only supplying the 'boost' not the full kVA.

277 to 277+69 is the same ratio as a 480V to (480+120)V. As topgone noted using a 480V transformer with a 277V supply is under-utilizing the full capability of the transformer. However this is perfectly safe to do, and 480V to 120V transformers are common and off the shelf.

In theory, 3 of these banked together would give you what you need: http://www.gordonelectricsupply.com...314~process~search~qdx~0~ds~dept~text~5914314

However this would need to be confirmed by ACME or a suitably licensed engineer.

-Jon
 

emiller233

Senior Member
Location
pittsburgh, pa
Your system under test has an input delta-wye transformer. This will pretty much isolate it from whatever the supply grounding is. In other words you input transformer would probably work just fine with a wye supply (600/346V), a 'high leg' , a 'corner grounded' system, or something else.

Your test specifications may limit the allowed supply, for example requiring a wye system balanced around ground potential or some other limiting factor.

The most blog standard approach would be a delta-wye isolating transformer, with the neutral of the wye grounded.

Autotransformer approaches will let you use smaller and off the shelf transformers, but this really needs to be engineered by a transformer supplier, not a web forum.

I suggested one possibility which gives an output balanced around neutral; topgone suggested one that is more efficient.

You won't find a 'delta-wye' autotransformer; since you don't have separate primary and secondary coils you have either delta or wye, not both at the same time.

-Jon

I have been trying to get in touch with the transformer folks, just haven't had any luck with them getting back to me yet. in the meantime, I'm trying to give myself a crash course in transformers ( as it is probably long over due for me to do this)

I'm looking at this now, I'm still trying to catch up up all of the suggestions from you guys over the weekend. i was out of town and didn't get a chanc...
 