AFAIK there is no such beast. You cannot have one end of the coil connected to two places at once!is the delta-wye autotranformer acceptable?
Sent from my XT1585 using Tapatalk
AFAIK there is no such beast. You cannot have one end of the coil connected to two places at once!is the delta-wye autotranformer acceptable?
AFAIK there is no such beast. You cannot have one end of the coil connected to two places at once!
Sent from my XT1585 using Tapatalk
this machine is fairly basic, it is a 'Test Bench' for testing an Air Compressor off of a train.
this transformer will power up a 480V 3-phase air conditioner (3.4FLA) and a large 330VDC Power supply (30KW) http://www.signaltestinc.com/product-p/sga 330-91.htm. Off the top of my head, this thing takes around 41A (I'd have to double check that #). so i need about 50A total
the control circuits are thru a separate 120VAC feed...
we looked into a mobile generator, and are willing to do this (that was priced into the job). the only thing is we may need to keep it much longer than we thought so the price would be quite a bit higher. that's why we are looking into using a transformer (that we could also use in the future if needed)
The power supply alone takes around 78A at rated load.
The AC is likely around 30A with locked rotor which is what is relevant when you're comparing line sag during start up.
Transformers look plentiful if you can source from Canada. There's a 112.5 kVA 2% z available now. If you can sort out freight and getting it through customs.
https://www.kijiji.ca/b-ontario/600-480-transformer/k0l9004
Power factor:
>0.69 typical for 440/480 VAC input (40V, 60V - 800V models, 0.9 available with modification “PF”)
I used 0.69. The value you use depends on if your rig was ordered with the modification they mentioned
For the AC, 30A is around the appropriate value to use for voltage drop. The voltage available with 30A added is what's available for motor while starting which isn't a big deal.
Initially you didn't give much details so my comments didn't exclude the possibility about something like a 40 hp motor that must start across the line under full load where the transformer impedance becomes a big deal.
is there a difference between a autotransformer, and a wye-wye autotransformer? or is it the same thing (which i believe it is)
An autotransformer has a _single_ tapped coil circuit, an 'isolating' transformer has two separate coil circuits, primary and secondary.
wye-wye would imply two circuits.
makes sense now that i see it!
The Hammond Power rep said they only have Wye-Wye Autotransformers, is he just using the wrong wording?
The Y075PKCN3L0U doesn't get connected to the neutral, and your load doesn't require a neutral.
You bring three phases 480V plus egc (PE in your drawing) to this transformer, and three phases 600V plus egc to your load.
-Jon
thank you!, just wanted to verify...
are there typically lugs in these big transformers for the EGC's to land?