I have a immersible pump with a new 480v contactor that chatters on startup what could be the cause ?
What is the rating of the pump motor?I have a immersible pump with a new 480v contactor that chatters on startup what could be the cause ?
I have a immersible pump with a new 480v contactor that chatters on startup what could be the cause ?
See post #2I'll jump over about 5 questions and get to my guess.
Under sized circuit to the pump, so turning on the pump makes the voltage drop more than 20%, that makes the contactor coil drop out, which alleviates the load, which allows the the voltage to rise again, which allows the contactor to close again, which brings in the motor, which drops the voltage again, repeat ad nauseum until the coil burns out, the contacts weld, the motor fries, or any combination of the above.
Do I win?
See post #2
Brevity is the soul of wit.Yes, but the way Jraef wrote it up was way more entertaining!![]()
Correct coil voltage?
A pressure switch that's bouncing around can cause some grief. Bugs or plain wore out.
I'll jump over about 5 questions and get to my guess.
Under sized circuit to the pump, so turning on the pump makes the voltage drop more than 20%, that makes the contactor coil drop out, which alleviates the load, which allows the the voltage to rise again, which allows the contactor to close again, which brings in the motor, which drops the voltage again, repeat ad nauseum until the coil burns out, the contacts weld, the motor fries, or any combination of the above.
Do I win?
HenceThose are my thoughts. To start with, where is the coil getting its control voltage from? It may have a 480v coil or likely a 120v coil using a 480-120v CPT. In either event the 480 is probably sourced from a 480v L-L which supplies the starter. You may be experiencing a voltage drop which affects the starter coil by causing it to not be pulling firmly. That is the first place tI would start.
If it only chatters on startup, I'm in the crowd that says too much voltage drop. Once motor has accelerated current will drop and voltage will rise to an acceptable level - so it runs just fine, there is just too much drop during starting.I have a immersible pump with a new 480v contactor that chatters on startup what could be the cause ?
Yes, I agree. That could explain it. But what if was say, a 2.2kW (3hp) motor on a stiff supply?If it only chatters on startup, I'm in the crowd that says too much voltage drop. Once motor has accelerated current will drop and voltage will rise to an acceptable level - so it runs just fine, there is just too much drop during starting.
Chattering happens in manual type contactors also.I'll jump over about 5 questions and get to my guess.
Under sized circuit to the pump, so turning on the pump makes the voltage drop more than 20%, that makes the contactor coil drop out, which alleviates the load, which allows the the voltage to rise again, which allows the contactor to close again, which brings in the motor, which drops the voltage again, repeat ad nauseum until the coil burns out, the contacts weld, the motor fries, or any combination of the above.