480 v contactor chattering at start up ?

Status
Not open for further replies.
Chattering happens in manual type contactors also.
During chattering the contactor does not drop out. Otherwise the pump would have stopped. During chattering the current continues to flow and pump motor picks up speed.
Yes.
Another thing that hasn't been addressed is contactor inrush current. Until the pole faces meet, the coil current can be very high. Until that dies away, the contactor can sound quite noisy.
 
This is why I started by saying I was jumping ahead by 5 guesses... in reference to the "20 questions" game comment before that.
In the absence of more information, that's all we can do.

I'm taking it that a lack of follow-up by the OP is a sign of my being the winner! :D:cool:
 
This is why I started by saying I was jumping ahead by 5 guesses... in reference to the "20 questions" game comment before that.
In the absence of more information, that's all we can do.

I'm taking it that a lack of follow-up by the OP is a sign of my being the winner! :D:cool:
I would take it as a lack of follow up...........:p
 
Or it's a faulty contactor. Or it's just noisy on inrush.
Maybe Smithy will come back and reveal all.

Maybe he needs to tell us what he means by "chatter".

Most of us have assumed that chatter means it is rapidly cycling in-out as in not enough voltage to keep it held. If problem goes away once motor has reached normal operating speed, sure seems voltage drop during starting would be the most obvious thing to look into first.
 
Maybe he needs to tell us what he means by "chatter".

Most of us have assumed that chatter means it is rapidly cycling in-out as in not enough voltage to keep it held. If problem goes away once motor has reached normal operating speed, sure seems voltage drop during starting would be the most obvious thing to look into first.
The long and the short of it is that the paucity of detail precludes any precise diagnosis.
 
Answer 21

Answer 21

I'll just keep guessing, answer 21. If it is for a sump pump, I gave seen them (cycle) chatter because it was oversized. Starts up and drains sump, shuts off, check valve not working and pumped up water comes back down pipe to sump. Repeat repeat repeat.
 
A water logged pressure tank can cause some rapid cycling, not sure if I would call it chatter but we don't know what the OPs definition is either.
I wouldn't either.
That would be more like a clock ticking rather than a machine gun type chatter.
We just don't know.
 