480 volt / 277 volt lighting
cornbread
I'm working at a plant where in the olden times they use 480 single phase to power 277 volts power lighting circuits (no neutral), just 480 volt to ground. Note the ground wire is insulated back to the panel (kinda of acting like a neutral). I know this is bogus today but was it ever legal ? I'm talking some 40 years ago. Are these types of installations grandfathered? Or is this just a royal screw up?
Why are you calling it a ground? Do you mean grounded conductor? Or is it the equipment ground? Chances are it is a neutral (Grounded Conductor).
If the wire is white, it's a neutral and it's legal If the wire is green, it's an EGC and it was never legal.
The MCC that feeds the lightinh panel is fed from a xfmr with a grounded Wye 2ndary. The feeds to the lighting panel is 3 phase with a ground. Looks like they made a neutral at the panel. So the return path from the neutral at the light goes back to the lighting panel but from the lighting panel to the MCC / transformer use the ground.
a learning opportunity
i ain't much when it comes to xfmrs, just curious what the name plate says on yours. i have several 480 delta - 208 wye LPs. x1 , x2, x3 = 208 3p xo neut. with EGC. x1, x0 = 110. or do you have a zig zag connected 480 - 277 lighting set up, with center tap neut.??? is raceway used for EGC???
I'm really confused by this description.
Unless you have something totally off the wall, 480 volts is obtained from two separate phase conductors, whether the service or downstream transformers are connected delta or wye.
Perhaps you may be dealing with a corner grounded delta. But in that case you are not dealing with an EGC, you are dealing with a grounded phase.
Is that ground insulated?
If so, it is a neutral... and it is grounded... and it is a 480Y/277 system. Line to line = 480V... Line to Neutral = 277V.
Also, I believe there are some instances in which the neutral was (is?) permitted to be bare.
From the light to the panel the ground/neutral is insulated, from the panel to the MCC its not, from the MCC to the XFMR its not.
If the system is 480 volts to ground as you stated then how can it power a 277 volt lighting circuit. Do you mean it is 277 volts to ground. That is common today.
cornbread said:
Its 480 phase to phase and 277 phase to ground.
Why are you calling the insulated wire from the panel to the light "the ground".
The ground wire is usually the green conductor or possibly bare conductor that does not ordinarily carry current. It is the grounding conductor. The white wire is the grounded conductor but sometime called a neutral.
What is it that you have? The white wire with a phase conductor is still legal today. You see it often with fixtures that have a 277 volt ballast.
just following along
most of my xfmr experience is 480 - 208 delta wye and 480 - 240/120 control.
don't use any 277 lighting. what type of xfmr is the op refering to. all i can find for 277 is zigzag connected with center tap gnd.
could someone enlighten me?
(no highjack intended, just curiosity)
Where is the system [intentionally] earth grounded? That is, where is(are) the grounding electrode system(s) bonded to the grounded conductor?
What type of raceway encloses the feeder between MCC and lighting panel?
Is the feeder a cable or individual conductors?
Is what you call the "ground wire... (kinda of acting like a neutral)" in any way bonded to non-current carrying metal parts at the load end?
The xfmr secondary is 480Y/277. OP'er has not stated primary voltage or configuration.
Look again. Just by telling us that they are 277 volt fixtures leads me to believe you have a neutral and one of the phases feeding the light fixture.
You can for sure use 480 to feed a light fixture but, when you mentioned the 277, that kind of got me. What type of ballasts and fixtures are they?